In Reply to: there is only one ground for the two lines.. posted by DC STEVE on June 27, 2007 at 20:34:58:
Please detail a bit more. From your description, it sounds like he used a 10/3 cable. I've seen 12/3 in my house, and I installed a run of 8/3. Both have a ground wire, a neutral wire, and two hots..a red wire, a black, a white, and either green or copper ground.
If this is the case, then they are sharing a common neutral. If you put one amp on each hot leg, then there will be no neutral current.
If this is the hum cause, it will only get worse when the amps are being used, as the draw will be some glorious (hideous) combination of neutral currents and hot currents..
If you have him switch both legs to the same side of the service, then the neutral currents will be the sum of the two hots.
I'd have approached it the way Ted Smith's setup was done, wires in conduit with a honker ground run for the whole shebang (If I recall correctly). But you should ask him, as it's been a while since we discussed it.
Cheers, John
This post is made possible by the generous support of people like you and our sponsors:
Follow Ups
- interesting - jneutron 06:50:24 06/28/07 (13)
- RE: interesting - Ugly 22:23:55 06/28/07 (12)
- RE: interesting - Ted Smith 07:28:20 06/29/07 (11)
- RE: interesting - Ugly 13:25:27 06/29/07 (10)
- RE: interesting - Ted Smith 14:55:14 06/29/07 (9)
- RE: interesting - Ugly 22:28:07 06/29/07 (8)
- Wiring possibilities... - Al Sekela 13:36:24 06/30/07 (3)
- RE: Wiring possibilities... - Ugly 10:58:16 07/01/07 (2)
- A single ground wire is preferred if possible. - Al Sekela 14:48:24 07/01/07 (1)
- RE: A single ground wire is preferred if possible. - Ugly 14:05:12 07/02/07 (0)
- RE: interesting - Ted Smith 12:18:59 06/30/07 (3)
- RE: interesting - Ugly 08:40:40 07/01/07 (2)
- Well :) - Ted Smith 12:43:15 07/01/07 (1)
- Cool. Small world eh? - Ugly 11:41:40 07/02/07 (0)