In Reply to: Cobalt rewire 240 V to 120 V posted by valvesonly on March 14, 2007 at 22:09:28:
Take a look at the Hammon Page describing dual Primary connections. In terms of a scheamtic, Pete pointed out an implementation commonly used using a double-pole double throw swittch,below:
The series winding connection is for 240V while the parallel connection (switch to left) is for 120V.
Hope this helps...fella Ontarian,